Hi ... I'm the original poster. I've been in the field all day, and just got back, and there seems to be some confusion about the configuration. I'll try to clear it up.
The home is 2-story, Sq.Ft.=3,100, Year Built=2007.
There is a main service panel mounted on an exterior wall of the home. This panel has the following breakers (see pictures):
Ckt# Description
1/3. 2-Pole 125 Amp Main.
2/4. 2-Pole 40 Amp A/C Condenser.
5/7. 2-Pole 40 Amp Sub-Panel.
6/8. 2-Pole 30 Amp Dryer.
10. 1-Pole 20 Amp Washer.
12. 1-Pole 20 Amp Gas Dryer.
13. 1-Pole 20 Amp AFCI Smoke Alarm.
14. 1-Pole 20 Amp Lawn Sprinkler.
The Sub-Panel is mounted on an interior wall of a built-in (attached) garage, and provides all of the circuits for the following:
Ckt# Description
1. 1-Pole 20 Amp Disposal.
2. 1-Pole 15 Amp Hall Lighting.
3. 1-Pole 20 Amp Dishwasher.
4. 1-Pole 15 Amp Bedroom #4 AFCI.
5. 1-Pole 20 Amp Gas Furnace.
6. 1-Pole 15 Amp Master Bedroom AFCI.
7. 1-Pole 20 Amp Microwave.
8. 1-Pole 15 Amp Bedrooms #2 & #3 AFCI.
9. 1-Pole 20 Amp Kitchen GFCI #1.
11. 1-Pole 20 Amp Bathroom GFCI.
13. 1-Pole 20 Amp Dining Room Lighting.
15. 1-Pole 20 Amp Water Softener.
17. 1-Pole 20 Amp Refrigerator.
19. 1-Pole 20 Amp Kitchen GFCI #2.
21. 1-Pole 20 Amp Game Room Lighting.
23. 1-Pole 20 Amp Garage GFCI.
25. 1-Pole 15 Amp Lighting & Plugs.
27. 1-Pole 15 Amp Lighting, Utility, Garage.
29. 1-Pole 15 Amp Living Room.
31. 1-Pole 15 Amp Family Room.
As stated earlier, the garage sub-panel is fed by a 40 Amp breaker on the exterior service panel. The neutrals & grounds are isolated from each other in this panel ... that's why I referred to it as "separately derived". If I've misused this term, I apologize. I've also attached photos of the panels with the covers off. The sub-panel feeder conductor is multi-strand AL. I was unable to determine the size (I'm not quite experienced enough to ID these by sight). I've attached a close-up of the conductor. Perhaps you can tell.
To Re-state:
- I was wondering if the 40-Amp Sub-Panel disconnect is large enough as I usually see Sub-Panel disconnects rated at 60 Amps.
- Is there any code being violated here? I had thought that 225.39(D) would address the issue, but I'm not sure.
Anyway, I hope all of this helps you to help me.
Thanks again.
Peter Sullivan
National Property Inspections
Round Rock, TX
The home is 2-story, Sq.Ft.=3,100, Year Built=2007.
There is a main service panel mounted on an exterior wall of the home. This panel has the following breakers (see pictures):
Ckt# Description
1/3. 2-Pole 125 Amp Main.
2/4. 2-Pole 40 Amp A/C Condenser.
5/7. 2-Pole 40 Amp Sub-Panel.
6/8. 2-Pole 30 Amp Dryer.
10. 1-Pole 20 Amp Washer.
12. 1-Pole 20 Amp Gas Dryer.
13. 1-Pole 20 Amp AFCI Smoke Alarm.
14. 1-Pole 20 Amp Lawn Sprinkler.
The Sub-Panel is mounted on an interior wall of a built-in (attached) garage, and provides all of the circuits for the following:
Ckt# Description
1. 1-Pole 20 Amp Disposal.
2. 1-Pole 15 Amp Hall Lighting.
3. 1-Pole 20 Amp Dishwasher.
4. 1-Pole 15 Amp Bedroom #4 AFCI.
5. 1-Pole 20 Amp Gas Furnace.
6. 1-Pole 15 Amp Master Bedroom AFCI.
7. 1-Pole 20 Amp Microwave.
8. 1-Pole 15 Amp Bedrooms #2 & #3 AFCI.
9. 1-Pole 20 Amp Kitchen GFCI #1.
11. 1-Pole 20 Amp Bathroom GFCI.
13. 1-Pole 20 Amp Dining Room Lighting.
15. 1-Pole 20 Amp Water Softener.
17. 1-Pole 20 Amp Refrigerator.
19. 1-Pole 20 Amp Kitchen GFCI #2.
21. 1-Pole 20 Amp Game Room Lighting.
23. 1-Pole 20 Amp Garage GFCI.
25. 1-Pole 15 Amp Lighting & Plugs.
27. 1-Pole 15 Amp Lighting, Utility, Garage.
29. 1-Pole 15 Amp Living Room.
31. 1-Pole 15 Amp Family Room.
As stated earlier, the garage sub-panel is fed by a 40 Amp breaker on the exterior service panel. The neutrals & grounds are isolated from each other in this panel ... that's why I referred to it as "separately derived". If I've misused this term, I apologize. I've also attached photos of the panels with the covers off. The sub-panel feeder conductor is multi-strand AL. I was unable to determine the size (I'm not quite experienced enough to ID these by sight). I've attached a close-up of the conductor. Perhaps you can tell.
To Re-state:
- I was wondering if the 40-Amp Sub-Panel disconnect is large enough as I usually see Sub-Panel disconnects rated at 60 Amps.
- Is there any code being violated here? I had thought that 225.39(D) would address the issue, but I'm not sure.
Anyway, I hope all of this helps you to help me.
Thanks again.
Peter Sullivan
National Property Inspections