Actually there is no minimum bending radius in the NEC for any conductor operating at less than 1000 volts.There's a minimum radius required for all bends. Someone smarter than me can tell you what they are.
Then you have distance as a function of voltage. What's your voltage on those conductors?
Have you asked Schneider how this works?
Actually there is no minimum bending radius in the NEC for any conductor operating at less than 1000 volts.
I don't see a real issue in the picture.
AFCI's fitted into an older Square D cabinet (QOBW-20). Is there a minimum clearance needed between the breaker lugs the sides of the cabinet?
That looks like a PIA.
The CH is not quite as bad. GE is a lot better.
I hate Square D AFCI's. I've switched to Siemens/Murray now.
You mean you are paying for AFCIs? :lol::lol:
We are working with insulated conductors and not PCB traces. We are working under the rules of the NEC and there is no bending radius for the conductors in that picture.There's a minimum industry chamfer as a function of voltage in PCB design.
The distance between the exposed terminal and the grounded conductor enclosure is more than sufficient for the voltages involved. UL 508A says 1" through the air is sufficient for 600 volts systems. It appears that we have more than one inch between the bare terminal and the side of the enclosure.As to distance, the insulation probably takes care of that for the insulated part of the conductor but not for the bare unless you want to count paint as an insulator. Put that lug too close to the sidewall and you have a problem.
I agree that they should answer the question, but I don't see any issues. Sure there is a reduction in the available wire "gutter" space, but I am sure that the space in not even close to being filled to the maximum of 40% that is permitted by the code.OP has a valid concern. Schneider should answer his question.
:?:blink:
I agree that they should answer the question, but I don't see any issues. Sure there is a reduction in the available wire "gutter" space, but I am sure that the space in not even close to being filled to the maximum of 40% that is permitted by the code.
I agree in a practical sense but listing wise is this breaker shown on the panel labeling as an acceptable breaker? The panel may predate even the concept of AFCIs.
The panel may predate even the concept of AFCIs.
I could have put it better.
I just meant you, the confirmed AFCI hater has had to install AFCIs.
I usually use square D, maybe ill check out some other brands as suggested. Peter D what do you like about the siemens?
I like that the AFCI's are the size of a standard breaker and therefore not eating up the gutter space unlike the Square D, CH-CH and older BR do. I also like that they use solid wire for the pigtail which makes it much easier to keep the panel neater. Finally, I like the indicator lights that tell you what caused the last trip.
Which brand are you referring to ? ITE ?