kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
What about "weak fuses"?
I recommended the breaker swap as a troubleshooting method, not a permanent repair tactic.If you test the current and determine the breaker is tripping when it should not then you replace or repair. The challenge is a test source but in troubleshooting you use your standard tools. If you find it trips when it shouldn’t based on measurements THEN you replace.
Weak wire too.What about "weak fuses"?
Well the jack stand from HF could easily be either situationWeak wire too.
"weak" is likely just the wrong word to use. It's more of a "functional issue" which can be many things, from poor manufacturing to extreme environmental's to improper install.
"He broke the bat,,,,, the bat was too weak", or it's probably more like the bat was made faulty, or, used incorrectly.
"The jack stand from HF broke and collapsed, must have been a weak weld", or more likely putting 2000lbs on a 1200lb jack stand was the issue.
What about "weak fuses"?
I get told by customers quite often that a breaker must be getting weak or "there must be a short somewhere" even though no overcurrent device is tripping in the latter one.
Most tripping issues I have encountered when the load is otherwise within acceptable range is excessive heating in/on or at bus connection/load terminal of the breaker.
If it is a circuit that actually is overloaded frequently, then you can sort of wonder if something inside hasn't worn out and is contributing to problems even when there isn't actual overloading going on, though that seems to be a little rare to encounter at least with the four main manufacturer's products that are still in production today.
Not exactly. NEC requires us to size them at 125% of the load for continuous loads. Non continuous loads they can be sized at 100%.Breakers in a panel are 80% rated unless they are 100% duty. I’ve run into this with Siemens.
Guessing (SWD) rated breakers have higher number of rated switching operations? Which is basically all 15 and 20 amp single pole miniature breakers anymore.There is a difference between the number of operations a breaker is rated for, and how many times it can TRIP. Yes, an MCCB 100A and under is rated for thousands of operations (6,000 under full load + 4,000 no load), but that "full load" is not about TRIPPING, it's only about the mechanical operations and contact life.
Under UL489, an MCCB 100A and under is only required to trip 50 times at 600% current. After that the calibration may be affected and it may start nuisance tripping. In this test sequence, if the breaker trips FASTER at 600% current on trip #50 compared to trip #1, that is stall a PASS. It is just required to trip WITHIN that the stated trip curve range, which if you look at it is wider than most people realize. Tripping at the lowest end of the range still meets the requirement.
But MORE IMPORTANTLY, it is only required to trip and reset TWICE under Short Circuit conditions. The mag trips are NOT designed for multiple tripping events and maintaining accuracy.
So can a breaker get "weak"? Defining "weak" is nebulous, but it CAN begin to nuisance trip if it is required to trip over and over and over.
That has to be defect or malfunction of mechanical items when that happens, or even foreign material that has gotten in there over time interfering with mechanical operation.The weirdest think I’ve seen are breakers tripped on the on position. Breakers fail all the time on small percentages. I will say they come defected from factory and fail mechanically just like anything else. But on my deducting reasoning/ troubleshooting the breaker is the last thing I expect to fail and the first thing I check.
Sent from my iPhone using Tapatalk
It could be be that neither of the trips is faulty and there is a different discrepancy.The simplest troubleshooting for a trippy breaker is substitution. Swap it for another one in the panel of equal rating and see if it keeps happening.
I'm pretty sure that the old standard for SWD ratings was rolled into the basic testing requirements for all breakers now, i.e. all breakers 20A and under are SWD rated now. The endurance testing difference for SWD rating was done at 100% Power Factor, HID rating was done at .75 power factor (meaning the breaker would actually see more current on switching). The UL 489 endurance tests are all done at .75 power factor now. The number of operations in the test standard is now what used to be the SWD numbers as well, so there really is no difference, other than the marking on the breaker, which is still done because the NEC says it has to be there.Guessing (SWD) rated breakers have higher number of rated switching operations? Which is basically all 15 and 20 amp single pole miniature breakers anymore.
When I was in school our class got to go to Square D plant that made QO breakers at that time (pretty sure they are put together in Mexico now)
One interesting part was the testing lab. they did let us watch a test, presuming AIC testing as they had a small loadcenter plugged in a 3 pole breaker with short leads (maybe 6 or 8 AWG) tied together to cause three phase bolted fault. They then closed a heavy door and applied power. Was a pretty loud bang. Opened door smoke was still lingering, carbon all over everything, reached in and reset the breaker - it did mechanically reset, but didn't look like you would want to use it again.
Not enough experience back then to ask some the questions I would ask now, but still very interesting even to this day for me.
I'm pretty sure that the old standard for SWD ratings was rolled into the basic testing requirements for all breakers now, i.e. all breakers 20A and under are SWD rated now. The endurance testing difference for SWD rating was done at 100% Power Factor, HID rating was done at .75 power factor (meaning the breaker would actually see more current on switching). The UL 489 endurance tests are all done at .75 power factor now. The number of operations in the test standard is now what used to be the SWD numbers as well, so there really is no difference, other than the marking on the breaker, which is still done because the NEC says it has to be there.
From what I've heard, the old QO plant in Lexington, KY is still there churning out breakers, just not as many as in Mexico. This came up in the recent discussions about reported shortages of QO breakers due to the Mexico plants having to reduce production.
But MORE IMPORTANTLY, it is only required to trip and reset TWICE under Short Circuit conditions. The mag trips are NOT designed for multiple tripping events and maintaining accuracy.
Apparently the AFCI's are mostly coming from Mexico as they are one of hardest items to get right now from what I have heard. I haven't needed any, but do have a new home project coming up.Isn't that two trips at full rated AIC?
In my ancient copy of NEMA-AB1, the was a difference between a Instantaneous Trip test (typically 10X frame size) and an Interrupting Test at full AIC.
Residential breakers used to be primarily built in Lincoln NE. Industrial breakers were built in Cedar Rapids IA. The Lexington KY plant builds loadcenters and safety switches, I first toured it in 1978 and breakers residential breakers were not being built there.
Even as far back as the early 80's the residential breaker lines were also being built out of the US, in places like Ireland. I have no idea the primary source of those products today.
No. They are tested a certain number of times
there is very little you can do to shorten a breaker's life