Plus OP said he has 8 feet of FMC - which is beyond the 6 feet permitted to use the raceway only as the EGC, so he is going to have a EGC inside the flex anyway.
It's only 8 inches not 8 feet
Plus OP said he has 8 feet of FMC - which is beyond the 6 feet permitted to use the raceway only as the EGC, so he is going to have a EGC inside the flex anyway.
He then threatened to go to the job, take pictures of the installation and send it to the state and basically said they would take my license away because I don't know codes.
The back of the cabinet is cut out several inches around the box. It's only Sheetrock behind the cabinet and the box is flush with the Sheetrock. No need for box extension.
314.29 Boxes, Conduit Bodies, and Handhole
Enclosures to Be Accessible
Boxes, conduit bodies, and handhole enclosures shall be installed
so that the wiring contained in them can be rendered
accessible without removing any part of the building or, in
underground circuits, without excavating sidewalks, paving,
earth, or other substance that is to be used to establish the
finished grade.
Well it occurred to me after I posted that it seemed like a lot of flex for what you described doing with it.It's only 8 inches not 8 feet