farmantenna
Senior Member
- Location
- mass
dwelling unit. 2020 code 240.21?
400 amp service rated ATS with single breaker outside the house. Two individual 4/0 AL SER feeders going from back of ATS to two individual flush mounted 200 amp MB panels 30' inside the house. The SER has 2/0 AL ground wire.
Appears to be non compliant tap. There's a 200 amp feeder on a 400 amp circuit breaker. I think it will be safe because the ground is large enough for the fault current and the feeder and panel load will be limited to 200 amps. This type of installation has been passed by two different inspectors.
I ask for your opinions.