I think it's an old Edward's fire alarm. Edwards Signaling has been around since 1872. Here's a link on their company history:
https://edwards-signals.com/index.cfm?pg=21&level=50&sid=0
I think it's an old Edward's fire alarm. Edwards Signaling has been around since 1872. Here's a link on their company history:
https://edwards-signals.com/index.cfm?pg=21&level=50&sid=0
Could be either one really, they can look similar. The simple tell would be that if it's an older Edwards Adapt-A-Bell unit, that dome is the bell and will ring if you tap it. If it's a spot heat detector, that's the chamber cover and it will not ring like a bell.That's an old Rate-of-Rise detector, probably a combination Fixed Temperature/Rate-of-Rise. Saw them a lot in warehouses.
A quick image google search seems to support that. Good job.
A quick image google search seems to support that. Good job.
I believe the ones I'm running across are still active and operational.
I doubt any of the modern electronic heat detectors will last as long.
Many modern addressable heat detectors use RTD's, sometimes in pairs. That's a pretty bullet-proof technology.
... electronics, semiconductors, microprocessors, and such. Eventually, that will probably die from heat or surges.
...in use for 70 years, ... I'm guessing they are nothing more than a fusible chunk of metal that melts at a specific temperature - probably a lot like a motor overload.
I don't think anything addressable will last that long.
Many modern addressable heat detectors use RTD's, sometimes in pairs. That's a pretty bullet-proof technology.
I kind of agree with steve66. What is bullet proof about the addressable unit is if you lose communication you get a trouble signal and something will likely fail before it is 50-70 years old. I still see those old units like OP is asking about in schools sometimes. Especially in storage areas or attics that need heat but not smoke detection.Maybe, but as soon as you say "addressable", I think electronics, semiconductors, and microprocessors, and such. Eventually, that will probably die from heat or surges.
I think these heat detectors have probably been in use for 70 years, and they probably have an another easy 70 left. I'm guessing they are nothing more than a fusible chunk of metal that melts at a specific temperature - probably a lot like a motor overload.
I don't think anything addressable will last that long.
I kind of agree with steve66. What is bullet proof about the addressable unit is if you lose communication you get a trouble signal and something will likely fail before it is 50-70 years old. I still see those old units like OP is asking about in schools sometimes. Especially in storage areas or attics that need heat but not smoke detection.
That's exactly correct. The fixed temp only ones have the little dimple in the center painted white if it's a 136 degree unit and white w/ black dot if it's a 190 degree unit. The fixed temp ones are a one shot deal if you trip them but the rate of rise units are resetable if you use the hand friction method as previously described. You can also look at the label on the side of the unit.That's an old Rate-of-Rise detector, probably a combination Fixed Temperature/Rate-of-Rise. Saw them a lot in warehouses.
I kind of agree with steve66. What is bullet proof about the addressable unit is if you lose communication you get a trouble signal and something will likely fail before it is 50-70 years old. I still see those old units like OP is asking about in schools sometimes. Especially in storage areas or attics that need heat but not smoke detection.
The rate of rise units are easily tested if they are accessible by step ladder. Rub your hands together to warm them up and put your palm on the dome. The delta T is sufficient to set them off.
Yes, these are in several schools.
Don't tell the kids that!!![]()