Jim W in Tampa
Senior Member
- Location
- Tampa Florida
Thanks, lot of good advice.
My load on the still working load just went drastically down because all the 240 loads just died. They were 2 x 3 1/2 ton units, another 5 ton unit, 2 ton unit, water heater 4500,water pump 2 hp, hot tub, So load went way down instantly.
What could have stayed up were all the lights and 120 receptacles and 6 x 1/2 ton wall units on 120 and 3 x 1 ton wall units on 120. So likely less than 100 amps.
The idea of center off i like because this system would be used if on backup gen for long outages in huricane to balance loads
A tie handle would be required per nec but only cause of chance of unskilled electrician ever touching it and that day will come as i am 62
Will not assume both legs are dead and we do know when power is restored both are live once again
Am thinking this out carefully before and if i follow thru.
Would run switches from my office in EMT from 2 main sub panels. Run would be 20 feet and because of derating #10 would only be switching maybe 6 important areas.
Might prove to be more trouble than its worth.
Sound system stayed up as it is on UPS with 2 marine battery. Some of the 120 wall units could been simply pluged in on another plug on live side.
Will be creating a drawing for all my electric because it would drive even a good electrician crazy figuring what i have.
I think there is a web site out there to help do load calcs, does anyone have link.
I started to do as Bob suggested and it will be hard with my unusual loads and could be over 200 amps if i don't shed the unused loads.
My load on the still working load just went drastically down because all the 240 loads just died. They were 2 x 3 1/2 ton units, another 5 ton unit, 2 ton unit, water heater 4500,water pump 2 hp, hot tub, So load went way down instantly.
What could have stayed up were all the lights and 120 receptacles and 6 x 1/2 ton wall units on 120 and 3 x 1 ton wall units on 120. So likely less than 100 amps.
The idea of center off i like because this system would be used if on backup gen for long outages in huricane to balance loads
A tie handle would be required per nec but only cause of chance of unskilled electrician ever touching it and that day will come as i am 62
Will not assume both legs are dead and we do know when power is restored both are live once again
Am thinking this out carefully before and if i follow thru.
Would run switches from my office in EMT from 2 main sub panels. Run would be 20 feet and because of derating #10 would only be switching maybe 6 important areas.
Might prove to be more trouble than its worth.
Sound system stayed up as it is on UPS with 2 marine battery. Some of the 120 wall units could been simply pluged in on another plug on live side.
Will be creating a drawing for all my electric because it would drive even a good electrician crazy figuring what i have.
I think there is a web site out there to help do load calcs, does anyone have link.
I started to do as Bob suggested and it will be hard with my unusual loads and could be over 200 amps if i don't shed the unused loads.