The condenser unit also requires two things.
1) Service access as required in the Mechanical Codes, typically the same 30" by 36" as in the NEC.
2) The same 30" by 36" working space at the electrical equipment access area to the condenser unit.
On that style (shape) of condenser unit, the service access and electrical equipment access area is at the corner, with the removable access cover wrapping around the corner.
The best way to provide that space (service access space and working space) for those units is to install the units so the service access corner is not facing the wall.
If you were to take the one in your photo, rotate 90 degrees counterclockwise, you would now have all clearances required.
3) Space must be as in 1) or 2), unless shown differently on the installation instructions.
I have seen some shown with even more space required, some with less space, many show that 30" by 36" space.
Then, of course, there is the clearance from the wall, etc., as required by the installation instructions, which, being as it is a piece of electrical equipment, must also be installed in accordance with its listing and labeling, i.e., in accordance with the installation instructions.
Clearance from wall, clearance from another a/c condenser unit, clearance above, not under roof runoff, etc.