Is this an acceptable use of a meter socket enclosure according to the UL Listing for this product?
Only an inexperienced and unqualified person with little knowledge of wiring and rules as per NEC 90.7 would try to add a line side tap to the lugs on the top of this meter socket enclosure --- let's face it there just isn't enough room no matter how you look at it!Originally posted by charlie:
The enclosure is a wide place in the conduit, it is not service equipment. If someone wants to make a splice or tap, they must have enough room and meet the requirements of the Code. I don't see what the listing has to do with the amount of room available in an enclosure. We would not permit that installation on our system but we maintain control of the meter fitting.
Joe, what is the purpose of your posting?
Originally posted by joe tedesco:
Only an inexperienced and unqualified person with little knowledge of wiring and rules as per NEC 90.7 would try to add a line side tap to the lugs on the top of this meter socket enclosure --- let's face it there just isn't enough room no matter how you look at it!
It is a violation
You know the location of this meter why not call the inspector or the power company and discuss your concerns with them?
[ February 18, 2005, 04:09 AM: Message edited by: iwire ]
Crossing the neutral $$ eh!Of course you could be right, the conductors could be just double tapped on the on the line side terminals and money passed to get it approved.
Jim:Originally posted by jim dungar:
Two meter sockets like this, once were common in Wisconsin and Michigan. The "second" socket was for electric heating, in particular 30A hot water heaters, which was billed at a different rate. I have no idea how the tap was performed, but one recent POCO manual infers it as two wires in one lug.
Forgot to ask:
Joe, why do you care if this installation is in violation of the UL Listing? NRTL listing are guidelines/suggestions not laws/requirements.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
Joe we all know that, what we do not know is the listing of that meter.Originally posted by joe tedesco:
I found the answer to my question, just as I suspected!