Assume a Sq. D EZ meter pack with a 1,000AMP MCB connected to (6) 225AMP meter sockets each with separate 225A MCB feeding individual tenant spaces.
Does the code allow me to feed the 1,000AMP MCB section with (3) parallel runs of 4#350KCMIL (separate raceways) for a total conductor ampacity of 930 AMPS.
I think "NO" because 2002 NEC 240.4(C); 230.42; and 230.90(A) say you can’t.
However, if I replaced the 1,000AMP MCB with a wireway this could be achieved as there are a total of 6 main disconnects. Assuming the total load is less than 930 AMPS.
Comments?
Does the code allow me to feed the 1,000AMP MCB section with (3) parallel runs of 4#350KCMIL (separate raceways) for a total conductor ampacity of 930 AMPS.
I think "NO" because 2002 NEC 240.4(C); 230.42; and 230.90(A) say you can’t.
However, if I replaced the 1,000AMP MCB with a wireway this could be achieved as there are a total of 6 main disconnects. Assuming the total load is less than 930 AMPS.
Comments?