Is this an electrode?

Is this an electrode?

  • Yes

    Votes: 0 0.0%
  • No

    Votes: 1 100.0%
  • AHJ call

    Votes: 0 0.0%

  • Total voters
    1

jxofaltrds

Retired ESI
Location
Mike P. Columbus Ohio
Occupation
Creator
At the end of this video they show rebar to be installed. My question is - if this rebar meets the requirements - does it require being used? Yes, no, depends on the AHJ? The link is to a construction video.

 
The building is new so it should already have a CEE.

From 250.52(A)(3)

If multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
Not to mention they missed putting it in the footer.
 