Not to mention they missed putting it in the footer.If multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
If rebar encased in concrete is an acceptable electrode (I don't know that it is) why wouldn't slab rebar be acceptable?The rebar is for the slab so it isn't an electrode
It's not an electrode if it's not in the footer or foundation.If rebar encased in concrete is an acceptable electrode (I don't know that it is) why wouldn't slab rebar be acceptable?
(3) Concrete-Encased Electrode
A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
Metallic components shall be encased by at least 50 mm (2 in.) of concrete and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth or within vertical foundations or structural components or members that are in direct contact with the earth. If multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system.
- One or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (1/2 in.) in diameter, installed in one continuous 6.0 m (20 ft) length, or if in multiple pieces connected together by the usual steel tie wires, exothermic welding, welding, or other effective means to create a 6.0 m (20 ft) or greater length; or
- Bare copper conductor not smaller than 4 AWG
OK, but the answer in #3 was "The rebar is for the slab so it isn't an electrode". Is a slab not the foundation?It's not an electrode if it's not in the footer or foundation.
I*t is not a footer and that is what the code states.OK, but the answer in #3 was "The rebar is for the slab so it isn't an electrode". Is a slab not the foundation?
But Roger's quote from the code says, "Metallic components shall be encased by at least 50 mm (2 in.) of concrete and shall be located horizontally within that portion of a concrete foundation or footing that is in direct contact with the earth or within vertical foundations or structural components or members that are in direct contact with the earth." It doesn't say that it must be in the footer, only that the concrete must be in direct contact with the earth. Am I missing something?I*t is not a footer and that is what the code states.
A slab is not a foundation or footing. I guess they are worried about a vapor barrier under a slab.Am I missing something?
Agree. A footing is a structural element defined by the building code, a slab isn't one.A slab is not a foundation or footing. I guess they are worried about a vapor barrier under a slab.
-Hal