I do not agree. Exception #2 states:
Exception No. 2: Where two to six service disconnecting
means in separate enclosures are grouped at one location
and supply separate loads from one service drop, set of
overhead service conductors, set of underground service
conductors, or service lateral, one set of service-entrance
conductors shall be permitted to supply each or several
such service equipment enclosures.
I agree the wording is somewhat ambiguous from the "several such" part, but I believe that is just referring to components within the single group. I have never seen such an installation where there are ungrouped groups of disconnects just scattered around a building, and cant recall anyone saying I can do that.