Is this copper only?

Status
Not open for further replies.

Sea Nile

Senior Member
Location
Georgia
Occupation
Electrician
IMG_20221005_094012556~2.jpg un the field right now,. We grabbed a split bolt to extend a ground in a panel that was cut too short. Instead of just blindedly usung it, I looked to see if we could use it for aluminum wire. I don't think we can
 
But found this on the web:

Description
Blackburn 350HPS 350 Aluminum/Copper Split Bolt
Technical Description: Split Bolt Type; Electrolytic Tin Plated Copper Spacer, Tin Plated Copper Alloy Bolt/Pressure Bar Material; 1/0 AWG Stranded, 1/0 AWG (ACSR) min. Run Conductor Size; 350 kcmil, 266.8 kcmil (ACSR) Max. Run Conductor Size

UPC: 78378685508

Part Number: 350HPS

Manufacturer: BLACKBURN
 
The connector would have Al, Al/Cu if it was suitable for Aluminium conductors. The one shown seems to be listed only Cu, and not usable on Aluminium wire.
Regardless of what box or mfg might print in publications inspector might call it out.
Been finding a lot of items that packaging is not matching product inside of package. (A whole case of receptacles package marked as TR but the product was not marked or even had the TR shutters.)
 
If I were an inspector I would reject it for use with Aluminum.
 
All the pics
 

Attachments

  • Screenshot_20221005-104337.png
    Screenshot_20221005-104337.png
    1.2 MB · Views: 23
  • Screenshot_20221005-104402.png
    Screenshot_20221005-104402.png
    1.4 MB · Views: 26
  • Screenshot_20221005-104433.png
    Screenshot_20221005-104433.png
    1.3 MB · Views: 26
  • Screenshot_20221005-104451.png
    Screenshot_20221005-104451.png
    1.3 MB · Views: 26
  • Screenshot_20221005-104517.png
    Screenshot_20221005-104517.png
    1.3 MB · Views: 22
Always considered the brass/bronze split bolts copper only & the plated or aluminum one if so marked being AL/CU.
 
IMG_20221005_094012556~2.jpg un the field right now,. We grabbed a split bolt to extend a ground in a panel that was cut too short. Instead of just blindedly usung it, I looked to see if we could use it for aluminum wire. I don't think we can
Nope.
See here:
 
I know an electrician who connected nine three phase PV inverters to a service with aluminum conductors using copper only listed lugs and burned up all 27 of them. We cut one of the burned lugs open and found a black resistive layer that had formed between the conductor and the lug. Resistance caused heat, and heat accelerated formation of the resistive layer - a positive feedback loop. He was lucky not to have caused a fire.
 
View attachment 2562413 un the field right now,. We grabbed a split bolt to extend a ground in a panel that was cut too short. Instead of just blindedly usung it, I looked to see if we could use it for aluminum wire. I don't think we can
You could just tap a lug into the panel and terminate at the top of the box.
 
I didn't think of that, I did however let the office know about it. They are sending a crew back to fix the issue and were glad I caught it.
Keep up the good work and paying attention. You’ll go far by challenging yourself to do things correct and not just going along with the common Joe.
 