Re: is this correct?
It sounds like we are getting in trouble again using un-defined terms like "subfeed".
In general,
The NEC says all branch and feeder conductors must be protected where they receive their supply unless they meet one of the exceptions (commonly called the tap rules).
All lighting and appliance branch circuit panelboards must have not more than two main devices on their supply side (the conductor OCPD may be used to meet this requirement).
Now, what do you mean by "must be sub fed"?
Are you dealing with service conductors? Or feeders?