Cliffhanger Revealed: My Opinion
Cliffhanger Revealed: My Opinion
Not that it's going to take anyone by surprise, but here is my opinion: 230.7 does not apply to this installation.
For one, the temp is
listed as a complete unit, meter and all, so the entire box is one enclosure. Therefore, an enclosure cannot be a raceway to itself, IMO.
The entire enclosure is listed as service equipment, so I cannot see how installing service conductors into this single service enclosure can possibly violate the NEC (which all but disregards that meters exist anyway).
Second: Let's say for a moment that we disregard the first item and consider them two independent enclosures. The principle that service conductors are not in the same box as the panelboard is not correct: There are service entrance conductors
feeding the top of the panelboard. Therefore, if the conductors running to the top of the meter socket are in violation of 230.7, then so are the service entrance conductors.
Third: The principle that the meter can disconnect conductors is not supported by the NEC. So to consider the conductors at the bottom of the meter entering the panelboard area of the enclosure "safer" from a disconnecting standpoint is not enforceable, by the NEC.
Fourth: The principle that the protective guards installed in Overhead/Underground convertible metermains are to conform with 230.7 is not correct, IMO. It is not a safety imperative, IMO. It is simply to prevent tampering, to protect the POCO's unmetered conductors, and ensure that they are getting paid for all electricity consumed at the premises served.