Senior Member
- Location
- Raeford, NC
OK here is the outcome I spoke directly to Ron Chilton from NC DOI and I also produced pictures of the service. He stated that although there are no wall under a pier built home it is still considered in the building envelope, I said OK i'll install the meter on the adjacent side of column which actually would be the exterior of the dwelling went up the outside 4 ft and then in with the same SEU. He said that was fine and so did the inspectors after I told them if they insist on a disconnect on the exterior then they have to take it up with the DOI. I am happy I just had to pull out the SEU and meter and remount took about 1 hour. I guess that would actually be the building envelope just thought it had to have enclosed walls but its done. Thanks very much guys Rich.
Good deal. I'm glad it worked out for you.