Smart,
That same lightning event may jump to a metal drain pipe while its at it, but, I would not
call the metal drain pipe a grounding electrode.
True... but it is more true of a local lightning event. Lightning surges can travel on electrical lines (distribution included of course) for miles, and it's generally all solidly connected on the grounding conductors.
I do agree with your lightning path, but, I
do not think that it was designed for that purpose, any more than the drain pipe. JMO.
The problem isn't in the purpose for which it is designed. The problem stems from the code trying to separate the issues of fault grounding and earth grounding. The fact that a conductor is a conductor is a conductor cannot be refuted by any amount of text.
For the record, it was one of the respected members of this Forum that posted the
comment about EGC and GEC are seperate items...
They are separate
issues, i.e. fault grounding and earth grounding. The NEC attempts and does a fairly good job at making them separate
items. However, current don't really care what the NEC calls a particular conductor. It just uses whatever is available.
There are many other instances besides the example provided earlier. For example, an enclosure securely fastened to structural steel with conductive means. The enclosure is grounded by way of a [fault grounding] EGC and the structural steel is grounded by way of an [earth grounding] GEC. When an local lightning causes an electrical surge on the enclosure, does the current travel on the GEC, EGC, or both? If a fault occurs in and to the enclosure, does the current travel on the EGC, GEC, or both?