Is this service 1PH or 3P - Keep getting conflicting answers

Status
Not open for further replies.

arnagas

Member
Location
Florida
Please refer to attached.

When I see this riser diagram I see a 3 Phase 1200A Meter Main.

I have someone telling me the following "[FONT=&quot]The plansindicate the main is 120/240 which is single phase. The 4 sets is the number of conduit and the (3) is the quantity of the wires."

[/FONT]
I am not sure how they are going to land 4 sets of conduit on a single phase breaker. But maybe I am missing something

Who is right?
 

Attachments

  • Capture.JPG
    Capture.JPG
    57.8 KB · Views: 0

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Please refer to attached.

When I see this riser diagram I see a 3 Phase 1200A Meter Main.

I have someone telling me the following "The plansindicate the main is 120/240 which is single phase. The 4 sets is the number of conduit and the (3) is the quantity of the wires."

I am not sure how they are going to land 4 sets of conduit on a single phase breaker. But maybe I am missing something

Who is right?

Where do you see three phase? Whoever drew it up crossed a zero, which is often done to distinguish it from the letter O; is that what you are seeing as the letter phi?
 
Last edited:

Ingenieur

Senior Member
Location
Earth
Confusing
3 each 4" conduits (they only show 3 conduits, not 4)
but 4 sets x 3 conductors? (Should be 3 sets x 4 conductors?)

likely 1 ph L1, L2, N

could be ea conduit 3 ph plus N?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Seems very clear to me that it's 1Ø because there are 3 SEC's in each raceway. Not sure why someone would think otherwise.
 

Ingenieur

Senior Member
Location
Earth
Seems very clear to me that it's 1Ø because there are 3 SEC's in each raceway. Not sure why someone would think otherwise.

3 conduits
12 conductors (they say 4 sets of 3, should be 3 sets of 4?)
4 conductors per conduit

if 4 conduits (they show only 3) then 4 sets x 3 makes sense
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
3 conduits
12 conductors (they say 4 sets of 3, should be 3 sets of 4?)
4 conductors per conduit

Why would there be 4 conductors/conduit if it's single phase? Unless I'm missing something I see nothing to indicate that it's 3Ø.
 

Ingenieur

Senior Member
Location
Earth
Correct it only shows three conduits but it clearly says 4 sets of 3-500's in each conduit.

4 sets of 3 500's per conduit? 12 500's per conduit?

I read it as 4 sets of 3x500 in 3 conduits
makes no sense
3 sets of 4x500 in 3 conduit
makes sense

confusing
 

kwired

Electron manager
Location
NE Nebraska
You would think the utility would want to supply this with three phase, unless the load just isn't there and/or it is in too remote location with no three phase readily available.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
You would think the utility would want to supply this with three phase, unless the load just isn't there and/or it is in too remote location with no three phase readily available.

I was just about to say the same thing. I don't think many utilities will provide a 1200 amp single phase service.

I'd say there is a good chance Ingenieur is right, and its a typo.
 