Is this service 1PH or 3P - Keep getting conflicting answers

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
yep
that is why it makes no sense
3 conduit with 4x500 each (3 sets of 4-500's)?
as shown nothing adds up
we can assume 4 conduit but it clearly shows 3

The missing line representing the conduit is the only thing that doesn't make sense. Everything else points to 4 sets of 3 conductors and single phase.
 

kwired

Electron manager
Location
NE Nebraska
I was just about to say the same thing. I don't think many utilities will provide a 1200 amp single phase service.

I'd say there is a good chance Ingenieur is right, and its a typo.
I upgraded a 2000 amp single phase service about a year ago to three phase, 208/120. But the load wasn't there, POCO only had a 100 kVA transformer supplying the single phase service. HVAC load was being added and we did need three phase. I ended up putting in a 1200 amp three phase service - POCO still only had 225 kVA transformer when done though. I bet the place seldom ever sees over 450 amps for peak demand.
 

Ingenieur

Senior Member
Location
Earth
The missing line representing the conduit is the only thing that doesn't make sense. Everything else points to 4 sets of 3 conductors and single phase.

they took great care to draw 3 lines
why not 1 line and tag it as 4 sets x 3 conductors each set in a 4" conduit?

it could easily be read as 3 sets x 4 conductors in 3 conduits (they show 3 conduits but state 4sets x 3 conductors)
L1 in 1 conduit
L2 in one
N in one
which doesn't make sense since they would need derated if even allowed

there is a conflict/error
an RFI will clear it up, we are guessing
 

Davidson Electrical

Principle @ Davidson Electrical Services LLC
Location
Tyler, TX
Occupation
Electrical Contractor
Correct it only shows three conduits but it clearly says 4 sets of 3-500's in each conduit.
has to be three phase if u have four sets of conductors at the main, but i have built quite a few services from drawings and never seen any funky drawings like that..
 