Is this wall oven okay on a 20 amp circuit?

Status
Not open for further replies.
I still don't see what allows a demand factor to be applied to a branch circuit supplying a single oven.
Note 4 to Table 220.55 states the branch circuit load for a single oven or cooktop must be the nameplate rating.
 