electricus
 - wisconsin
I have a 480V single phase 7.5kVA transformer, primary side is protected with a 15A breaker (that is what I have available).
According to Table 450.3(B) under the "primary only" "currents of 9 amps or more "125%" can I use the "not required" for the secondary protection. In other words I'm protected on the primary side at 125% (or less), I read it that I don't need secondary protection.
The panels are side by side, was trying to save on needed a main breaker in the small (6 space?) 120/240v panel.
Also as a side note when figuring current draw for this example. Just the very basics, if I have 480V, 15A single phase on the primary at 100% duty, then I will have 240V 30A single phase on the secondary. What is the current available for a 120V load, still 30A right?