Hey guys just need some conformation on article 338.12 B
Can USE cable ran in pvc raceway be terminated in a sub panel located inside a residence? The pipe comes up thru the slab about 4ft and into the panel. I interpret 338.12B 2 as saying it must terminate in an exterior j box and then maybe use SE cable or other type of wire to enter the building.
Thanks in advance for any clarification. I haven't done a lot of residential wiring in the past.