Is utility Closet in a bathroom good for service switch?

Status
Not open for further replies.

darekelec

Senior Member
Location
nyc
Assuming correct working space is achieved is it code compliant to install a service switch and a meter in a utility closet that’s in a bathroom?
it’s a 1 family house, 2008 nec with nyc amendments but the question is more about interpretation and logic of how to cathegorize the closet.
I say not possible but i would like to ask here.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Service disconnects are not allowed in bathrooms in dwelling units. 230.70 should be the reference.

I think the question is whether the utility room is considered in the bathroom. I would ask your inspector. My interpretation is if you cannot enter or leave the room except thru the bathroom then it is part of the bathroom... Authority having jurisdiction call.
 