I know of the violations but I can't count how many times I've seen 12/3 mc ran for an isolated ground circuit and they have used the red wire to yoke(without even attempting to reidentify the red wire).
If I'm not mistaken it's more so that any currents (that should not exist) on the system EGC/conduits will not bring electrical noise into the electronics that depend on the EGC to take any such noise out of the equipment.haskindm said:I believe that the main advantage of installing an IG circuit is that it allows you to take the IG ground through the sub-panel(s) and back to the ground/neutarl bar in the main service, thus by-passing any incorrectly installed sub-panels with neutral/ground connections.
This is very true. Remember that the isolated grounding conductor is still the only EGC available to the plugged-in equipment, and must return to the system neutral at the bonding point to clear faults.An IG circuit is NOT allowed to have the grounding conductor run to an isolated grounding electrode. This will create a very dangerous situatin with no way to clear a ground fault.
Well I think by now you should know what is true and what is fiction. Since this is a stick built house, he is already has IGR assumong NM and plastic boxes were used.mgmelec said:the installation is at a friends stick built home, device is for computer , ups, and associated equipment. friend read somewhere that isolated, insulated ground recep. is whats needed for his application.
This is not always true. Art. 200.7(C)(1)mgmelec said:i know re identifing conductors smaller than#6 is a violation, but ahj in my area will fail a job with a white hot leg such as an a/c disco.
mgmelec said:Why not reidentify red cond. green in certain situations. still not sure what general conscensus is.
chicar said:Trever,try 250.119