Seen too many times where after the install, another trade (usually sheet rockers) knock the boxes around on the studs, causing the locknut to loosen, fork lifts or other equipment damaging the pipe. One case in point, a big box store had a rack become energized because a pipe was pulled loose, and the hot cut into the pipe on the disconnected end. The breaker did not trip because the egc was the pipe. If a wire egc had been used, the breaker would have tripped. Luckily the customers were only getting a mild shock. But even though the rack was bolted to a concrete floor, it was not a low enough resistance to trip the breaker.