I was wondering if you could help settle an office dispute.
Given the "standard" dry type transformer connected as shown in the picture. (Picture from Ed in a previous post). What would you do differently if the 120/208 secondary panel was for an "isolated ground" system that consisted of only branch circuits that supplied only isolated ground receptacles?
In other words, if you have gone to the trouble and expense of having IG outlets and isolated ground bars in the panel, does it make sense to tie the primary system EGC and secondary system EGC to the metal case of the transformer. Second question, does the NEC give you any choice in the matter?
Lastly, if everything is run in metallic conduit, will the primary side grounding system be connected to the secondary side (the isolated) grounding system no matter what you do with the EGC? another reason i think isolated ground outlets are a waste of money.
Given the "standard" dry type transformer connected as shown in the picture. (Picture from Ed in a previous post). What would you do differently if the 120/208 secondary panel was for an "isolated ground" system that consisted of only branch circuits that supplied only isolated ground receptacles?
In other words, if you have gone to the trouble and expense of having IG outlets and isolated ground bars in the panel, does it make sense to tie the primary system EGC and secondary system EGC to the metal case of the transformer. Second question, does the NEC give you any choice in the matter?
Lastly, if everything is run in metallic conduit, will the primary side grounding system be connected to the secondary side (the isolated) grounding system no matter what you do with the EGC? another reason i think isolated ground outlets are a waste of money.