isolated ground GFCI?

Status
Not open for further replies.
I've looked, and never came across one. I've used GFCI breakers with regular IG devices.

Of course, depending on the specs and building type, romex and a plastic box can work with a regular GFCI.
 
Does any manufacturer produce an isolated ground GFCI?

Can U get a second green yellow conductor which would be 4th wire to it ? It'd be a isolated ground if a metal box and the correct receptacle is used (note triangle)
... Article 250.146 (D) & FPN...

Why this application, If I can ask?

805ecmCQfig1.jpg
 
cadpoint

Hypothetically speaking of course?

the print called for a dedicated isolated ground receptacle in a kitchen area. It would be located about four feet from a sink. The gfci breaker would solve the theoretical issue. I was just curious if a gfci isolated receptacle was in existence.

I looked around to know avail and figured I would check with others on this site. I find this code forum very helpful and informative.
 