Isolated Ground Help

Status
Not open for further replies.

BatmanisWatching1987

Senior Member
Location
NJ
Occupation
Jr. EE
I received the following comment from the local township and could use some clarification.
"Shows homerun to panelboard IG homerun panelboard IG schedule with demand and connected load is not shown per NEC 2017 Section 220"

I showed the new Panel as an Isolated Ground Panel and I connect all my POS or any equipment which requires a IG to that panel schedule. I also put the loads on the panel schedule schedule. Maybe the local township missed looking at the panel schedule since it was on a different drawing.

Where do I found information about panelboard loading in Section 220?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Sounds like they missed the panel schedule. Did it contain all of the information that they're asking for?
 