I have done it once, but other then that dont understand why whats the point. 2 grounds Jw the logic behind it i guess.
I have done it once, but other then that dont understand why whats the point. 2 grounds Jw the logic behind it i guess.
I have done it once, but other then that dont understand why whats the point. 2 grounds Jw the logic behind it i guess.
The argument is that having an isolated ground reduces common-mode noise that could interfere with electronics.I have done it once, but other then that dont understand why whats the point. 2 grounds Jw the logic behind it i guess.
If you have no wiring errors in the branch circuits or feeders an isolated ground is not needed.
Or any EGC under those conditions.
Please elaborate further... :blink: Not having any EGC would be a code violation.
If there are no faults or errors in the wiring there is no safety reason for an EGC. Just like if there are no faults or errors there is no need for OCPDs.
I think we are all well aware they are code required.
On the contrary, you can have small contributions to current on the EGC, such as equipment with EMI filters that put capacitance from line to ground, that add up to enough current on the EGC to cause enough voltage to make a hum problem on audio gear that uses a single ended input.I think what your saying is redundant for the sake of the argument.
My point is that if you do not have a code violations like standing ground faults an IG is not needed.
I think what your saying is redundant for the sake of the argument.
My point is that if you do not have a code violations like standing ground faults an IG is not needed.
And obviously I disagree.
I have absolutely no idea why you feel code violations determine the need for an IG.
And obviously I disagree.
I have absolutely no idea why you feel code violations determine the need for an IG.
On the contrary, you can have small contributions to current on the EGC, such as equipment with EMI filters that put capacitance from line to ground, that add up to enough current on the EGC to cause enough voltage to make a hum problem on audio gear that uses a single ended input.
If all of the participating devices are connected to IG receptacles, then they will only have to deal with the small amount of current that they put on the EGC and the problem will be reduced. Otherwise the small offset voltages can build up through the entire branch and feeder system.
Some might consider such noise filters and surge suppressors to be standing ground faults anyway, but UL and NEC do not seem convinced of that.
"(12) In particular, no attempt must be made during orafter installation to separate the electronic system?sequipment grounding conductors from the ac powersystem?s equipment grounding conductors and itsassociated earth electrode grounding connections.Such separations would violate the NEC andproduce potential electrical fire and shock hazards.They would also be likely to damage circuits insidethe related electronic equipment, or to at leastdegrade the operation of it.(13) Note that the use of the IG method even if it followsNEC requirements, does not always improve theperformance of equipment. In fact, the use of theIG wiring method is just as likely to make thingsworse or to result in no observable change to theoperation of the equipment. There is usually no wayto predict the benefits if any, of isolated groundcircuits except by direct observation andcomparison between solid grounding (SG) and IGmethods in each case.(14) It is relatively easy to convert existing IG circuits toSG circuits on an as-needed basis. On the otherhand, it is generally both impractical and not costeffective to convert an existing SG circuit to an IGstyle that conforms to NEC requirements.Accordingly, circuits used to supply power toelectronic equipment can be designed and firstinstalled as IG types, so that they may later beconverted back and forth between IG and SG asneeded."
You may have a point here, but being honest that generally holds true for exceptionally sensitive and I dare say possibly dated audio equipment.
Though there is nothing wrong with some older audio equipment, it still rocks on!
And yes, leakage current for suppressor is not an NEC concern, in fact they have occupancy censor that leak to ground a bit, but there is no limit to how many you can have on a circuit. Im sure that leaking will add up.
EMI filters and surge suppressors do leak to ground,
but not the degree a grounded neutral or 3 wire subpanel does.
But here is the deal, as soon as the equipment touches anything else that's grounded like a rack or its connected through shielded cables to other equipment you loose that IG.
A true IG application would not only need an isolated ground from the service disconnect or SDS, but all the equipment its connected to would need to be isolated on rubber supports away from anything else grounded. A true iso ground is rare if not impossible to achieve.
Consider cash registers in super markets. Yes, they like to spec an ISO ground. But as soon as the register comes in contact with the stand grounded through a regular EGC with a motor, light ect and other branch circuits forget about it. At this point you are wasting copper. In fact Id say 99% of applications don't need them.
What I am saying, is that if you had a code violation such a grounded neutral you will have audio hum or aka a dirty ground. People will notice that.
In the real world issues arising from dirty grounds have fomented the preference for an IG receptacles in an effort to eliminate ground loops. What no one was told was that dirty grounds were caused by wiring errors (NEC code violations).
If you don't have code violations you wont have ground loops,
That is what Big John was saying and I am saying the same thing. I am not sure why you are skeating around that.
That is not factually correct. Simply connecting your CATV, SATV, or aerial antenna creates a loop. Interconnecting audio device with ground referenced signal inputs creates loops. All those interconnections fully comply with NEC requirements. No IGR can fix it or remove the problem, most likely is does nothing or make it worseIf you don't have code violations you wont have ground loops, if you don't have ground loops you don't need IGs. Its that simple.