Does the NEC allow a single, isolated grounding conductor to be routed (from the same panelboard) between several IG receptacles or does each receptacle require its own isolated grounding conductor?
I suspect more will argue that they're not effective at all (given how and where they're often used).some argue that it won't be as effective
Zbang, would you say the benefit of having the IG is more psychological vs technical ? LolI suspect more will argue that they're not effective at all (given how and where they're often used).
These days, almost all electronic power supplies don't have cords with EGCs.Zbang, would you say the benefit of having the IG is more psychological vs technical ? Lol
They certainly benefit the installer.Zbang, would you say the benefit of having the IG is more psychological vs technical ? Lol
I agree. There is 0 benefit in 2025. Unless told otherwise I would use a single IG for as many circuits as I could to waste as little money as possible.I suspect more will argue that they're not effective at all (given how and where they're often used).
Actually, that was me, but who's counting?As Hal said, a lot of things now don't have/need an EGC now . . .
Art. 517 is about redundancy not anything about an IG. I pretty sure that some of the old IG requirements have been removed in the last two cycles.All, Does article 517 change this discussion? Or should I consider the IG a dinosaur and move on?
Sorry there.Actually, that was me
We are using the 2017 NEC on this project - 517.16 talks to IGR’s.Art. 517 is about redundancy not anything about an IG. I pretty sure that some of the old IG requirements have been removed in the last two cycles.
Don't be. I said the same thing many times in older posts.Sorry there.
Going off of memory - the IG receptacles are not allowed in patient care areas because they defeat the purpose of redundancy, i.e. the IG receptacle in the patient care area are more dangerous.We are using the 2017 NEC on this project - 517.16 talks to IGR’s.
But this is in reference to patient care so it probably doesn’t apply anyway
How about if we take one IG per circuit (to several receptacles) along with one EGC per circuit for along the same route from the panelboard ground bus?Skipping the rules part.
The IG conductor should follow the same path as the Hot & Neutral conductors.
The best plan is to Star out from a central junction box to all the receptacles and then a single cable back to the panel.
Do whatever you want. Isn't going to amount to a hill of beans.How about if we take one IG per circuit (to several receptacles) along with one EGC per circuit for along the same route from the panelboard ground bus?