HI. I am the inspector that jzombek6 is speaking of. I told Joe about this site, I really tell a lot of electricians about this site because it is a great site to gain information. I guess that article 250.146 (9D) does not state that it has to go all the way to the service disconnect. I copied and pasted the article below.
D) Isolated Receptacles. Where installed for the reduction
of electrical noise (electromagnetic interference) on the
grounding circuit, a receptacle in which the grounding terminal
is purposely insulated from the receptacle mounting
means shall be permitted. The receptacle grounding terminal
shall be connected to an insulated equipment grounding
conductor run with the circuit conductors. This equipment
grounding conductor shall be permitted to pass through one
or more panelboards without a connection to the panelboard
grounding terminal bar as permitted in 408.40, Exception,
so as to terminate within the same building or
structure directly at an equipment grounding conductor terminal
of the applicable derived system or service. Where
installed in accordance with the provisions of this section,
this equipment grounding conductor shall also be permitted
to pass through boxes, wireways, or other enclosures without
being connected to such enclosures.
( Thanks Again Jumper for the item you gave me, as you can see it can in handy )
I was going off of a Soars Grounding and Bonding book. This book shows both ways. The NEC says just to ? an Equipment grounding conductor terminal ? it does not say it has to go to the Service disconnect location. I corrected my mistake and said that it was installed as per design. The install is ok he did not have to change anything.
Thanks to everyone who posted.
Bill Annett