Re: Isolation of neutral at Sub Panels
Originally posted by eagle:
Can I get a simple explanation on the requirements and or need to isolate at the SUB.
I will try, a panel that is to be used as a "sub panel", (the code would call this panel
"Load Side Equipment") must not have any continuity between the enclosure and the ground bar
before any wires are connected to this panel.
Originally posted by eagle:
Question 1 : when testing for continuity at the sub .. I should find NO continuity between the branch circuit neutral and ground bar .. YES ... NO ?
There should be NO continuity between the branch circuit neutral and ground bar of a sub panel.
Until this panel is connected to the feeder, once you connect this panel to the feeder you will have continuity.
The voltage from your tester will flow from the ground bar at the sub panel down the equipment grounding conductor, back to the service panel and through the service panel common grounding / neutral connection and back up the neutral of the sub panel feeder to the neutral bar of the sub panel.
Originally posted by eagle:
Question 2 : If NO.. how is that avoided on sub panels that do not have the new type of stand off bars and they directly contact the panel frame ?
It can not be done with the panel you describe, that type of panel is for use as a service panel only, never to be used as a sub panel.
The two key codes about this, in my opinion are 224.5 which is the code article that prevents the use of the panel you describe with the neutral connected to the enclosure.
224.(5)Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
And 250.142(B) Which prevents us from running a just 2 (or 3) hots and a neutral to a "sub panel" and using the neutral as the grounding means, as of course this "sub panel" enclosure and all the branch circuits from it must be grounded.
250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
250.142(B) Load-Side Equipment.
Except as permitted in 250.30(A)(1) and 250.32(B), a grounded circuit conductor shall not be used for grounding non?current-carrying metal parts of equipment on the load side of the service disconnecting means or on the load side of a separately derived system disconnecting means or the overcurrent devices for a separately derived system not having a main disconnecting means.
One last thing, although many of us including myself often use the term "sub panel". that term is not in the code book at all.
This panel is treated the same as any other loads from a service panel it is in code terminology
"Load Side Equipment".
Meaning the load side of the service panel or service disconnect, that has the Bonding Jumper (Neutral/Ground Jumper)
I hope this helps, I have tried to keep opinions out and code references in, it is a tough subject to give a yes or no answer to.
Bob