I am working on a hospital project which has "dirty" power issue i.e. several small brownouts that affect the equipment and HVAC. The electrician installed a meter between the main switchgear and the two ATS's serving the equipment branches. Voltage sags were noticed continuously on the B leg without corresponding current swells, and the measurements indicate that the B leg is 1.7 degrees out of phase. The thought is that this could be an issue from the substation side, probably from the capacitor banks or switching?
Would isolation transformer be able to resolve the issue by avoiding those sags? I know they improve power quality, but I cannot see how those sags coming from the utility would not be reflected on the load side.
Any other recommendations to resolve such an issue?