I have received updated information recently with updated measurements - they said their current distortion exceeds the levels set by IEEE 519. They said that when they ran the calculations with 1500kVA transformer and 5% impedance, the Isc/IL value came out to 39.4 which puts a limit on TDD at 8%, but they need to know the exact transformer information to run the calcs with a precise Isc.
Is anyone familiar with this test and what it means? Honestly I have not done power quality analysis before.