Do others think this is a good scenario where an isolation transformer would be preferred over other means of fault reduction?
A transformer being used instead of a reactor in a 34.5kv subtransmission tap feeding 34.5kv distribution in an area with 34.5kv taking hold as a new standard. The trafo provides voltage regulation via on board tap changer without neutral phase shift (delta-wye instead of 3 wye connected 32 step tap regulators which sometimes give issues on long lines), does not pass zero sequence current, does not force a new neutral on the subtransmission, and- drum roll- limits fault current down to 10ka. The iso unit can be placed in the same yard as the 34.5kv-4.8kv or 34.5kv-12.47kv trafos.
VS
I can take 3 pole banks of the appropriate size and wire them wye grounded primary- closed delta secondary for my zero sequence source, add 3 32 step voltage regulator and then add a recloser after that getting my full T to D package at a lower cost. I could, and I've seen it done that way- but how would I control fault current in this case. Reactor in series?
Also of note/benefit since the power transformer can be ordered with primary taps and reconfiguration- it can be converted 69kv at a latter date.
Thoughts?
A transformer being used instead of a reactor in a 34.5kv subtransmission tap feeding 34.5kv distribution in an area with 34.5kv taking hold as a new standard. The trafo provides voltage regulation via on board tap changer without neutral phase shift (delta-wye instead of 3 wye connected 32 step tap regulators which sometimes give issues on long lines), does not pass zero sequence current, does not force a new neutral on the subtransmission, and- drum roll- limits fault current down to 10ka. The iso unit can be placed in the same yard as the 34.5kv-4.8kv or 34.5kv-12.47kv trafos.
VS
I can take 3 pole banks of the appropriate size and wire them wye grounded primary- closed delta secondary for my zero sequence source, add 3 32 step voltage regulator and then add a recloser after that getting my full T to D package at a lower cost. I could, and I've seen it done that way- but how would I control fault current in this case. Reactor in series?
Also of note/benefit since the power transformer can be ordered with primary taps and reconfiguration- it can be converted 69kv at a latter date.
Thoughts?