Isolation transformer

Status
Not open for further replies.
It's an isolation transformer. We don't know if the secondary star point is grounded.
Would be helpful to know that and why the need for an isolation transformer in the first place.
To reduce neutral currents transfromer primary. Transformer secondary point is grounded to bldg steel.
 
Last edited:
To reduce neutral currents transfromer primary. Transformer secondary point is grounded to bldg steel.
If primary is delta there will be no neutral to have currents in, even if you pulled a neutral with supply conductors there is nothing to connect it to.

Does your primary have an H0 terminal? If all it has is H1, H2, H3 it is likely delta primary winding.

If it is delta primary to delta secondary (three wire secondary) then the secondary is protected by the primary overcurrent device.
 
To reduce neutral currents transfromer primary. Transformer secondary point is grounded to bldg steel.
Can you provide a picture of the nameplate, the diagram, or the manufacturer's specification, please?
 
I realized its wye on about post #10 checked manufacturer site. Posted the link its not auto transformer.

Sent from my SM-G935U using Tapatalk
 
I realized its wye on about post #10 checked manufacturer site. Posted the link its not auto transformer.

Sent from my SM-G935U using Tapatalk
Most of the thread has been about verifying what you actually have. If it is indeed delta -wye your question was answered in post 2.
 
Where do you see delta to wye? Primary is 480V. Secondary is 480V/277V.

Sent from my SM-G935U using Tapatalk
It really doesn't matter what the secondary is, if the secondary has a neutral, the transformer primary OCPD cannot be used to protect the secondary conductors.
 
It really doesn't matter what the secondary is, if the secondary has a neutral, the transformer primary OCPD cannot be used to protect the secondary conductors.
Even though the secondary neutral is connected to ground of the isolation transformer?
 
Even though the secondary neutral is connected to ground of the isolation transformer?
The secondary is a separately derived system. There is no additional "ground" that is associated with the transformer, ground is defined in art 100 as "the earth". "Grounding" the secondary neutral is making the secondary neutral the same potential as earth, which was also done to the grounded conductor of the primary circuit at it's source, unless it is an ungrounded supply, so that makes both primary and secondary same potential at that point, however a grounded conductor that is a normal current carrying conductor isn't supposed to be "grounded" again at another location as a general rule - that can result in undesired currents over undesired paths.
 
It really doesn't matter what the secondary is, if the secondary has a neutral, the transformer primary OCPD cannot be used to protect the secondary conductors.

I was under the impression that single phase single voltage and 3 phase delta to delta could be protected by Primary OCPD. Does that rule out a 4 wire delta?
 