I'm surprised a 60/120V isolation transformer has not been mention yet. Perhaps it has without knowing it...? It is a supply configuration permitted for audio signal processing equipment. I believe it is also used in hospital operating rooms and in other situations utilizing sensitive electronic equipment. In short, with ground connected to the neutral point of the transformer secondary, the power supply system is "balanced". Being an audiophile, you should know the theory behind balanced vs. unbalanced signal transmission. Essentially the same principle applies to this power supply configuration.
Two NEC articles, in particular, will apply here:
- ARTICLE 640— AUDIO SIGNAL PROCESSING, AMPLIFICATION, AND REPRODUCTION EQUIPMENT
- ARTICLE 647— SENSITIVE ELECTRONIC EQUIPMENT
The transformer has a center-tapped 120V secondary winding (a separately derived system in Code speak). There are no line-to-neutral loads, so there is no need to run a neutral conductor to the disconnecting means (but not prohibited). The center tap (neutral point) is grounded at the transformer. Per 250.30 a supply-side bonding jumper is required. However, 647.6(B) permits an isolated equipment ground bus, clearly marked as "Technical Equipment Ground", connected to the grounded conductor (neutral) on the line side of the disconnecting means.
The 120V branch circuits will all be connected line-to-line, so each circuit requires a two-pole common trip breaker. All 15A and 20A receptacles are required to be GFCI protected and marked [see 647.7(A)(2)] Not required, but suggest running as isolated ground circuits and receptacles.
With that said, I have never set up such a system. My statements here are based my interpretation of Code, experience, and knowledge. As to Code requirements, the only section I'm having a problem with is 647.7(A)(4) regarding receptacles, which states "All 125-volt receptacles used for 60/120-volt technical power shall have a unique configuration and be identified for use with this class of system." Exactly what is meant by unique configuration? Do isolated ground GFCI receptacles qualify? I ask because...