So if this is just a blower motor on an air handler and you say is 2/3HP, 5.3A, what is that nameplate for? It clearly says 14A. You can't run 14A continuously on 14ga wire, so something is missing or the info is inconsistent in this puzzle.
i will verify the blower motor specs.
the plug wire did not seem to get warm during the initail temp test, but the socket box/cover did. i suspect i will be changing the socket to a hard wired breaker type, and changing the 14ga plug/cord over to 12ga cord (the end inside the unit connects to board via push on blade connectors, etc).
more to come.