First of all, I thank everyone who helped.
My question is in article 250.52.
I don't understand this correction from the inspector. I've done similar work on all my jobs, and I've never received a correction like this.
Article 250 tells me that Ufer is sufficient.
I don't know whether to appeal the correction or not. (It's just the inspector's whim, that's what I think). I'll have to lose around $1500 just to open the walls, run 4-gauge bare copper grounding wire, patch the walls, close the walls, and re-tint them, since the homeowner isn't at fault, right?
NEC 250.52(A), such as:
- Metal building frame
- Ufer ground (concrete-encased)
- Ground ring
- Rod/pipe electrodes
- Plate electrodes
- Other made electrodes
NEC 250.52(A)(3) — Concrete-Encased Electrode (Ufer Ground)
This describes a grounding electrode consisting of:
- At least 20 feet of
- Bare copper conductor #4 AWG or larger, or
- Steel reinforcing bar (rebar) ½ inch or larger,
- Encased in at least 2 inches of concrete,
- In direct contact with the earth.
What do you think is correct or not?