This is actually bugging me a little bit. This very rarely comes up in discussion in my work, it's generally a given that the point of connection to a "Metal Underground Water Pipe" per 250.52(A)(1) shall be made within 5 feet of the point of entrance to the building, but is that actually what the code says?
250.50 tells us that all qualifying electrodes described in 250.52(A)(1) through (A)(7) shall be connected to create the Grounding Electrode System. All good there.
250.53 says that if a water pipe is used as an electrode it shall have "Continuity" and a "Supplemental Electrode" is required. Okay, no problem. In the case of the OP's example, a CEE could be that supplemental electrode. Good so far?
250.53(D)(2) includes an exception that the supplemental electrode can be connected per 250.68(C)(1).
250.68 covers connections to Grounding Electrodes. It states that the GEC shall connect to the electrode per (A)-(C). 250.68(C) says that GEC’s and bonding jumpers “shall be permitted to be connected at the following locations and used to extend the connection to an electrode(s):
(1) Interior metal water piping that is electrically continuous with a metal underground water pipe electrode and is located not more than 1.52 m (5 ft) from the point of entrance to the building shall be permitted to extend the connection to an electrode(s). Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a conductor to interconnect electrodes of the grounding electrode system.”
Is that really saying they must connect to that electrode at that point, or is this only addressing the supplemental electrode connection? Is the “5-foot” rule present somewhere else that I’m missing?
Thanks.