HertzGood85
Member
- Location
- California
I recently installed (40) retrofit pole lamps fixtures on existing 22' parking lot poles. They have replaced the older 400 watt HID style lamps. The issue I am having is that when I did a shop test on the retrofit lights to check them out for issues before installing them, I found when they were energized if I disconnected the ground wire the whole can was energized with 120 volts ac. When I reconnected the ground wire to the two led drivers the 120 volts disappeared. The voltage setup that these pole lamps use are 2 legs of a 480 volts wye connected system. So basically, two hots and a ground. Has anybody come across this issue or does anyone understand why a 480-volt 2 leg system would displace 120 volts to the casing of the lamp when the ground is removed? Thank you.