Hi, Perhaps my post couldnt be understood since it is not so much clear..
I cant see why circuit breaker breaking capacity is defined with IT double fault and not with a simple NT single phase fault (voltage will be Phase-neutral of course ) ?
I wonder if this (1) Note is relevant to both 220 and 400 volt or just 400 volt?
If just 400 volt what might be the thing meant with it?
Can u see why 1P breaking capacities are given for IT schemes especially?
With an IT system (see Wikipedia) a phase to ground fault that will not trip the breaker, as the ground is isolated, so there will be a negligible fault current flow under these circumstances. But when a second phase to grounds fault happens (on a different phase, obviously) then there will be a phase to phase short, a double fault situation, and then the breaker will open.
Which is the what. But I dont know why...
okay forget it...
İn a schneider NG125H mcb data table it says
Type Voltage Breaking Capacity
1P 220...240 36000
1P 380....415 9000 (1)
(1) IT İsolated neutral system double fault 1P breaking capacity
so why is it so ?
is there any relation between the system and the capacity of a MCCB ?
Hi lads, Let me ask you one thing of this subject, Now we have a circuit and we calculate that this circuit will have 10 kA short circuit current, now if we use a P+N double pole MCB , so what will be the s.c rating of this mcb?
İf the answer is 10 kA so does it mean one of the poles will break the current even the other one doesnt or it means both pole have 5 kA breaking rating so that they break just half of the current since they operate at the same time? so will this MCB 5 OR 10 KA? can you englighten me?