I have ITE pushmatic panelboard that is installed single family home. Are ITE pushmatic panelboard not in compliance with any of the NEC 2014 code section?
Replace it. it's a dinosaur![]()
........ They were actually pretty well made.
If they were compliant at the time they were installed and remain in good working order, there is no NEC section that will require their replacement even if they would not be compliant today. NEC makes it very clear that the code/standard is NOT intended to be retroactive. Local governments may impose such requirements if so empowered.I know but as AHJ we need to see in code. I cannot find consumer product safety not sure what it’s called that says life cycle of breaker. Anyone have link?
1) Never seen Pushmatic bolt-ons cause arc damage at bus contact like most plug-in brands.I know but as AHJ we need to see in code. I cannot find consumer product safety not sure what it’s called that says life cycle of breaker. Anyone have link?
Nothing a HI says can be enforced by anyone. They have no legal authority to demand anything other than payment for services rendered.
AAA Inspection Group LLC said:Repair or Replace (RR) = The item, component or unit is not functioning as intended, or needs further inspection by a qualified contractor. Items, components or units that can be repaired to satisfactory condition may not need replacement.
Since AHJ's are never called to home sales, or house-flipper remodels, the lowly Home Inspector (HI) report is the only tool buyers have to force qualified contractors to investigate premises defect and hazards.
...........