If you have a 1x4 fixture in a hard ceiling (drywall metal studs) and the fixture is removable is this an acceptable means of access to the J-box?
The fixture is not part of the structure or finish. A j-box above a removable fixture is accessible.Accessible (as applied to wiring methods). Capable of being removed or exposed without damaging the building structure or finish or not permanently closed in by the structure or finish of the building.
Again, I don't see the fixture as being "part of the building".314.29 Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible
Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade.
No, It has to be accessible with out removing the light.
Our local AHJ's won't let us cover a box with a 1x4 flourescent light.
I think that is why they now make a large knockout in the back of some of these light fixtures. You put that over the box and your okay.
Now we are talking it is mounted right up against it, right?
If you are surface mounting an electric discharge luminaire take a look at 410.24(B) (2008)
I read the OP as the 1X4 luminaire being recessed in the hard ceiling.
Chris
The fixture is not part of the structure or finish. A j-box above a removable fixture is accessible.
Again, I don't see the fixture as being "part of the building".
Obviously the wording could be better.
So then which section would you cite as a violation?
I agree with Chris. Assuming a recessed fixture, there is no code violation.Obviously the wording could be better.
So then which section would you cite as a violation?
I agree with Chris. Assuming a recessed fixture, there is no code violation.
None, unless the fixture is a surface mount flourescent and then 410.24(B) (2008) or 410.14(B) (2005) NEC.
Again, if it is a violation to have a j-box above a removable recessed 1X4 fixture how would you install a recessed can?
Chris
The OP did say a fixture in a hard ceiling and that the fixture is removable. I would understand that to mean that the fixture is recessed and the box is adjacent to the fixture above the ceiling. When Sam checks back maybe we can get some clarification.
I agree that the OP was not describing this type of install, but now that you've brought it up .... I don't think a 3/4" ko is a "suitable opening...... to provide access to the wiring in the box". I think what you're describing is a violation of 410.24(B). But what the OP is describing is not a violation.Also, just so I fully understand the points being made, if I have a 1x4 surface mounted fluorescent light fixture, as long as that 3-4" knockout that comes with the fixture is placed over the junction box it is ok to "bury it" because it is accessible. This I agree with.
I believe Ron was talking about the 3 to 4 inch KO that many strip fixtures have in the back surface, not a 3/4" hole..... I don't think a 3/4" ko is a "suitable opening...... to provide access to the wiring in the box".
I believe Ron was talking about the 3 to 4 inch KO that many strip fixtures have in the back surface, not a 3/4" hole.
as long as that 3-4" knockout