To calculate pull box sizes, first multiply the largest conduit by six then add up the rest of conduit for width. for depth, largest conduit multiply by two. This is for splices.
For pull boxes 8x the largest conduit plus the sum of others.
314.28(A)2 Significant Changes Nec 2008
?????To calculate pull box sizes, first multiply the largest conduit by six then add up the rest of conduit for width. for depth, largest conduit multiply by two. This is for splices.
314.28(A)2 Significant Changes Nec 2008. this is a book.
This was also discussed in a continuing education class that i had last year, conductuded by a master electrician/contractor/instructor
Be more specific. You said two rows. What size raceways are in row 1? Are they on the same wall?so if you have a splice box with two rows of 3-1", 2-4", and 8-3/4", what is the size of the box needed to get the job done?specifically.
If you know the answer, then tell me. Why should I have to work the problem. :grin:row 1: 4", 4-3/4", 2-1"
row 2: 4", 4-3/4", 1-1"
into one side of box
row1:same
row2:same
coming out of box from left
splice box size?
i already know the answer......
The answer is 31x31x11, but since u can not order a box of that specific size then you have to get one that is 36x36x12. And you can not go lower.
So a 2 1/2" conduit would be 15x15x5, but since you can not get a box of that size, lower is not feasible. So 18x18x6 would be big enough.
I like and admire your Poise! I'm not trying to speak down on your skill level, I'm here to challenge you to do better--which I see you are capable of doing!thats the point, to show you can. not trying to argue. just was posting to what the OP had a question to. this how i calculate all boxes bigger than 1 1/4 conduit. plus you said you would calculate it.
infinity said:Where exactly are you getting the 2X dimension from in the NEC?