I did a little work at a brewery last week hooking up power to a new heating element in their 900 gallon hot water tank.
It’s a 9kW element at 240v 3P so it’s only pulling about 22 amps.
There’s 2 elements, both are 9kW in this tank.
The problem is that the heat given off by the tank when it heated up makes the ambient air temperature around the j-box very high and the wire insulation melts back to a point where things short out in the j-box, shorting out the element and tripping the breaker.
Here’s a picture of the old element’s j-box:
I’m not sure the best solution to the problem. I decided to upsize the wire to #8 and I used some heat shrink and added a layer of tape over the crimp connectors where the wire is crimped to try and mitigate the insulation melting issue.
I’m not confident that upsizing the wire is the best solution. The #10 wire is more than adequate for the current.
Any suggestions for an alternative solution would be much appreciated.
It’s a 9kW element at 240v 3P so it’s only pulling about 22 amps.
There’s 2 elements, both are 9kW in this tank.
The problem is that the heat given off by the tank when it heated up makes the ambient air temperature around the j-box very high and the wire insulation melts back to a point where things short out in the j-box, shorting out the element and tripping the breaker.
Here’s a picture of the old element’s j-box:
I’m not sure the best solution to the problem. I decided to upsize the wire to #8 and I used some heat shrink and added a layer of tape over the crimp connectors where the wire is crimped to try and mitigate the insulation melting issue.
I’m not confident that upsizing the wire is the best solution. The #10 wire is more than adequate for the current.
Any suggestions for an alternative solution would be much appreciated.