iwire said:BTW, 12/2 MC down to the fixtures on jack chain is a violation unless you happen to have stranded MC.
I have never been sited for this, where would I find this restriction.:-?
iwire said:BTW, 12/2 MC down to the fixtures on jack chain is a violation unless you happen to have stranded MC.
wireman3736 said:I have never been sited for this, where would I find this restriction.:-?
Back in post #17wireman3736 said:I have never been sited for this, where would I find this restriction.:-?
roger said:Larry, 410.28 (E) is the article and section
(E) Stranding Stranded conductors shall be used for wiring on luminaire (fixture) chains and on other movable or flexible parts.
stickboy1375 said:I really don't think the Code Panel had this in mind when they wrote it...
iwire said:I can't see that happening on most of the jobs, the ceiling guy would tell likely tell us 'fogeda aboud it'.
iwire said:I think it is exactly what they had in mind.
I have no idea which one of us is right.:smile:
stickboy1375 said:The only reason I have doubts, is that ART 410.28 is about protection of conductors and insulation, well if MC is not enough protection for conductors then I guess I'm at a loss...
mkgrady said:I guess my choices for the wire drops are some kind of rubber cord (SJ or SO)rated for 20 amps, stranded 12-2 MC if I can find it or 1/2 inch greenfield with #12 stranded thhn. The drops will be about 8-10 feet long.
JES2727 said:Well, I would use 3/8 greenfield with #12 stranded wire. That's exactly what I did, just a couple of weeks ago. I also made sure to locate the outlet boxes within 6' of the fixture. I see now, after re-rereading the book that I was in error. I was thinking of 410.67(C), which applies to tap conductors and limits them to 6' max. It does not apply to branch circuit conductors. But then again, are they tap conductors that run from the outlet box and terminate in the fixture? Or are they branch circuit conductors?
I agree that 410.28(E) prohibits solid wire for this application.
Do the rules for 12/2 MC (black/white/green) and 3/8" FMC with #12 (black/white/green) conductors differ?infinity said:Although branch circuit conductors have no length limit, 3/8" FMC has a limit of 6'. For a longer whip you would need to use 1/2" or larger.
LarryFine said:Do the rules for 12/2 MC (black/white/green) and 3/8" FMC with #12 (black/white/green) conductors differ?