LarryFine said:The bonding needs to be done whether or not the motor is double insulated.
I agree and add if there is any bonding to do anyway.
LarryFine said:The bonding needs to be done whether or not the motor is double insulated.
Because a GFCI senses current escaping the circuit a trips. If a person "stands in" for the neutral, then it will trip.wizzzard11 said:How can a gfci or a breaker trip if the nuetral and ground are open...
Because the inspector is either misinformed, or operating on an edition of the NEC prior to the 2005. This was clearly changed in the 2005, 680.74....and why do you think the inspector checks to make sure you hook the #8 solid ground wire to the cold water line (when the house is copper pipe)...
That's just silly. What is the difference between connecting to the hot and cold if they are electrically continuous?...and will make you change it if you put it on the hot line even though the pipes hook to the same parts (faucet)?
You need to calm down, there is no reason to get out of breath on this.You all need to use common sence and think about the potential out come on this issue.
If there is an Equipment Grounding Conductor (EGC) in the receptacle, and the cord to the motor, how is the housing of the motor going to become energized and not kick the breaker? We already have a conductor going back to the panel - the EGC, and that's all that's required.When you hook the ground clamp on the cold water at the tub and then hook to the motor lug this is a code violation and feel lucky if the inspector is passing your whirlpool wiring cause he or she could make you run it to the panel.
Have you encountered more loose connections in jetted tubs than the rest of the house?wizzzard11 said:When I wire a whirlpool sometimes I will locate the gfi at the access panel of the tub and in other situations sometimes a gfi breaker any way you look at it there is a hazzard weather the nuetral works it's way off the ground bar in the panel or loosens off the gfi recepticle...
So, you disagree with the Code Making Panel's decision to nearly eliminate all equipotential bonding requirements for jetted tubs, then? On what basis?...my point is a whirlpool may not be safe unless the #8 ground comes directly from the panels ground bar and all metal parts on the tub as well as the motor lug are hooked up.
Yes, I have. I've taken to using my drill to get the screws "tight", and then finishing off the final torque with a flathead screwdriver. GFI backwire screws in particular always seem to be plenty loose after just the drill.wizzzard11 said:Did you ever notice when you plug your wires into a gfi recepticle and go to tighten the screws but they just don't seem to get tight enough?
haskindm said:Hot tubs, hydro massage tubs, and swimming pools must be BONDED, meaning that all metal in the vicinity of the unit is connected together.
georgestolz said: