I would call the manufacturer of the device and see if that can be the issue. Back when we had this issue those units were much more expensive then what the inspector paid.
One of the AHJs for whom I worked supplied all the inspectors with AFCI tester (don't recall the manufacturer) and we experienced the same problem. On short runs, the tester worked reasonably well; on long runs or houses fed from a temporary, they seldom caused the breaker to trip even though the breaker test button functioned. The testers ended up in the trash bin.There was a local electrician who ran into this issue many years ago. It turned out that the tester wouldn't work properly when the run was over 75'. Since this is a large home I will guess that most circuits are over 75'
It was interesting because the inspector would test one receptacle and all was fine but when he move to the next receptacle it would trip. That second receptacle put the distance over 75'.
Yea...where does it say that!?Same reason a kitchen GFCI can't be under the sink.
It doesn't, however many inspectors will turn it down especially if it is to the back of the cabinetYea...where does it say that!?
This was an issue here in WA for dishwashers since a dualfunction 2 pole breaker isn't available and older dishwashers are often on multiwire circuit.. So there is a local amendment specifically allowing a gfi device in a sink cabinet. It's the only type of cabinet that this is allowed here though.It doesn't, however many inspectors will turn it down especially if it is to the back of the cabinet
Yea...where does it say that!?